Grounding for -Safety- and -Lightning-

Forgive me if I sound pedantic, or if I'm just plain dense. Two questions:

If I added a direct connection between the two groups of ground rods (even if this direct connection consisted of an additional four ground rods inline (12'-16' between ground rods) as well as the copper cabling required), this configuration would no longer pose an issue?

If I removed one of the groups of ground rods and instead used better feed line to make up for longer coax runs, would this be better? The current runs are about 75' end to end (grounding block near the building entrance for coax) for receive only.

I think you have an adequate number of ground rods in your design. Just bond them together, ideally outside, or if not, make sure both groups of ground rods are connected securely to your utility ground.
 