Electrician question

Mike-Mike

Instructor
Dealer
NES Member
Rating - 100%
26   0   0
Joined
Mar 16, 2008
Messages
8,960
Likes
1,460
Location
Shrewsbury MA
and even IF you did put in two 20 A breakers in the panel, how are you going to RETURN the combined 40A common current? Thru the 30A neutral wire you have???? it does not compute.

there might be a way of doing it with dual ganged 15 amp breakers....but consult an actual electrician on if that is legal.
Actually the "neutral" ( the grounded conductor) carries unbalanced current. So if one leg was pulling 10a and the other was pulling 8a there would be 2a on the neutral at the panel.
 

Spanz

NES Member
Rating - 100%
1   0   0
Joined
Feb 25, 2009
Messages
36,888
Likes
28,102
Actually the "neutral" ( the grounded conductor) carries unbalanced current. So if one leg was pulling 10a and the other was pulling 8a there would be 2a on the neutral at the panel.
hmmmm, i was wondering about that...since the currents are inversed in phase.
 

76Too

NES Member
Rating - 100%
47   0   0
Joined
Apr 4, 2013
Messages
5,751
Likes
4,759
Location
Inducky, Yusa
Why ham and egg the shit of it when u can pay a professional and just sit back and eat steak and eggs with a nice tall mimosa!! I bet that 2k would look mighty good if u burn your camper down, lol!
I understand what you’re saying, but i’m not sure you’re familiar with the fact that basically every serious camper has it’s own 50’ power cord ATTACHED to the inverter. Where’s the danger with that?
 

Asaltweapon

NES Member
Rating - 100%
50   0   0
Joined
Dec 21, 2008
Messages
15,593
Likes
8,941
Location
Northern Mass
and even IF you did put in two 20 A breakers in the panel, how are you going to RETURN the combined 40A common current?
Well if it was me I would just staple a white wire (if the walls and trim are white anyway) down the wall and follow the baseboard back to the CB panel.
OR....
Just use the bare wire because both the white and the bare ground ties into the same buss bar in the main panel anyway.

[banana][pot]
 

xjma99

NES Member
Rating - 0%
0   0   0
Joined
May 10, 2011
Messages
8,030
Likes
7,694
Location
NH
and even IF you did put in two 20 A breakers in the panel, how are you going to RETURN the combined 40A common current? Thru the 30A neutral wire you have???? it does not compute.

there might be a way of doing it with dual ganged 15 amp breakers....but consult an actual electrician on if that is legal.
First, he doesnt have a neutral wire, period.

Second, if he did have a neutral wire and changed the breaker to a 2pole 20, and was drawing 20 amps on each leg (not recommended, but just talking theory) then the current on the neutral would be zero amps. If he was drawing 15 amps on one leg, and 5 on the other, the neutral current would be 5 amps.

Anyways, based on the assumed level of electrical knowledge inferred from the OPs question, the correct answer is ‘don’t do your own wiring.’
 

Asaltweapon

NES Member
Rating - 100%
50   0   0
Joined
Dec 21, 2008
Messages
15,593
Likes
8,941
Location
Northern Mass
Just make sure when you measure the distance to determine the proper gauge wire you go all the way to the panel. It's also safe to go up one size to be sure. Nothing with electric motors is fond of extension cords because most people don't pay attention to the details.
For my air tools I'll run a longer air hose versus running it off a cord.
 

Spanz

NES Member
Rating - 100%
1   0   0
Joined
Feb 25, 2009
Messages
36,888
Likes
28,102
First, he doesnt have a neutral wire, period.
.’
"I can plug into my 3 prong Dryer outlet that would result in two 110v lines."

upload_2019-7-12_17-35-59.png
he has three holes in the outlet, +110V, -110V, and neutral. (By plus i mean 0 degrees phase, and - 180 degrees phase of the sine wave). In a dryer's case, almost all the current (the heater element current) comes from the +110V and returns via the -110V wire. But some, if there are any 110 V circuitry...like for the control board, would go back on the neutral wire. IF i remember correctly, the neutral is also connected to frame ground on the dryer.
 
Rating - 0%
0   0   0
Joined
Jul 10, 2016
Messages
2,835
Likes
2,956
Location
Hidden rebel base
First, he doesnt have a neutral wire, period.

Second, if he did have a neutral wire and changed the breaker to a 2pole 20, and was drawing 20 amps on each leg (not recommended, but just talking theory) then the current on the neutral would be zero amps. If he was drawing 15 amps on one leg, and 5 on the other, the neutral current would be 5 amps.

Anyways, based on the assumed level of electrical knowledge inferred from the OPs question, the correct answer is ‘don’t do your own wiring.’
Still can’t understand why he wants to go through all that when you can just easily pull a couple a new circuits
 

Woodsy

NES Member
Rating - 100%
15   0   0
Joined
Apr 6, 2009
Messages
5,417
Likes
2,507
Location
In the north woods likely hunting or trapping
Why ham and egg the shit of it when u can pay a professional and just sit back and eat steak and eggs with a nice tall mimosa!! I bet that 2k would look mighty good if u burn your camper down, lol!
If it was a camper yes that would be funny, it’s a two family on the coast so no, I’m not willing to take a chance. Just thought maybe there was some device that I could use but it appears not
 

Mike-Mike

Instructor
Dealer
NES Member
Rating - 100%
26   0   0
Joined
Mar 16, 2008
Messages
8,960
Likes
1,460
Location
Shrewsbury MA
Called an electrician but laughed my ass off on some of the replies. NES never lets me down ....well except for the Glock and Creedmoor lovers.
Theoretically you have enough conductors to wire a singe pole circuit. The issue is the wires are the wrong color a little over sized so it would be a shitty install.

You could take some white tape and wrap it around your red wire on each end, and wire up the oversized wires to a regular singe pole 20a breaker, install a 4" box with a receptacle and call it a day...

oh the death and dismemberment that would ensue...
 

MisterHappy

NES Member
Rating - 100%
15   0   0
Joined
Jul 28, 2009
Messages
22,328
Likes
7,564
Location
On the 16 yard line, shootin' for the Lewis!
Re the wrong wire colors: 220 single phase compressor. Professional electrician had used black and white wire, but since it was 220, the white was not neutral. I wrapped red tape on the ends at the switchbox, and the termination at the compressor termination, so the next person won't be surprised.

Good thing that a pro did it.
 
Rating - 0%
0   0   0
Joined
Jul 10, 2016
Messages
2,835
Likes
2,956
Location
Hidden rebel base
Re the wrong wire colors: 220 single phase compressor. Professional electrician had used black and white wire, but since it was 220, the white was not neutral. I wrapped red tape on the ends at the switchbox, and the termination at the compressor termination, so the next person won't be surprised.

Good thing that a pro did it.
Unfortunately a lazy pro
 
Rating - 100%
1   0   0
Joined
Feb 17, 2019
Messages
510
Likes
616
Location
Over the Hills and Far Away